Work concerning plumbing or sanitary water (hot, cold, clean or used). Management, access and use of water at home: drilling, pumping, wells, distribution network, treatment, sanitation, rainwater recovery. Recovery, filtration, depollution, storage processes. Repair of water pumps. Manage, use and save water, desalination and desalination, pollution and water ...
User avatar
delnoram
Moderator
Moderator
posts: 1322
Registration: 27/08/05, 22:14
Location: Mâcon-Tournus
x 2




by delnoram » 05/07/15, 20:18

yes I think we're going around in circles :|

Otherwise I found that : Arrowd: which brings us back practically
to the previous calculation

On an electric motor (Guinard water pump) from 750 W (1CV), 220V, 50 Hz, 1250 RPM: What value of starting capacitor should be adopted? The original value is no longer readable and with 16 micro Farad 400 V the engine refuses to start alone, it must be launched by hand.
Thank you for answering me.

You need about 56μF / 250V or 400V ...
0 x
"Thinking should not it be taught in school rather than to make learning by heart the facts that are not all proven?"
"It's not because they are likely to be wrong they are right!" (Coluche)
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 05/07/15, 21:38

Yes on.turn a little round: normal for a pump lol

Didiou 56 uF it's a lot ... all the 600 engines at 800w that I saw still had only 16 uF or 20 uF

Good if my multimeter seems to work I had a doubt: I measured a new capacitor from 2uF to 1,95uF ...

I ordered 4 capacitors: 10, 15, 25 and 40 uF ... history to do some tests and combinations in parallel editing
0 x
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 15/07/15, 12:18

Christophe wrote:I ordered 4 capacitors: 10, 15, 25 and 40 uF ... history to do some tests and combinations in parallel editing


Here I received the 4 operating capacitors for testing:

Image

The multimeter capacimeter gives about 15 μF for the 15 μF:

Image

The 2 other than I tested above were cooked ...

Anyone know why there are 4 outputs (the 2 G and D connectors are connected in the capacitor, we can wire it from 4 ways gd: up-up, down-down, up-up, up-down) ?

To easily do paralleling can be?

Image
0 x
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 15/07/15, 13:04

I will try the following editing: 10μF, 15μF, 25μF, 35μF (25 + 10), 40 μF, 50 μF (40 + 10) ...

I'll tell you from what capacity the pump restarts ...
0 x
User avatar
Macro
Econologue expert
Econologue expert
posts: 6524
Registration: 04/12/08, 14:34
x 1641




by Macro » 15/07/15, 13:31

That it redémre is a thing. That it maintains its regime in charge is another ... Reminder to charge a centrifugal pump:
it must be fed correctly (if possible with a height of fluid just below its axis) and have it flow freely with the largest flow possible it is in these conditions that it draws the most intensity.
0 x
The only thing safe in the future. It is that there may chance that it conforms to our expectations ...
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 15/07/15, 16:21

Just macro: I planned to do startup tests with a hydraulic load ...

I no longer remembered that the maximum power of a pump was with the minimum discharge height (logically physically it should be harder, so more amperage, start a pump with X m of water column above no ?).

In short thanks for this reminder. I will try like this (with a wattmeter taken to control consumption).

This pump will be mounted on a suppressor group tank with pressure switch ... once repaired it will therefore turn between 1.5 and 3 bars approximately.

ps: what is on it is that considering the volume of the capacitor of origin, this one had not more than 20 μF ...
0 x
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 16/07/15, 15:43

I just tested all the capacitors on the engine, it does not work better: whether the capacitor is connected or not, the motor reacts the same: it blocks at startup between 0 and 2 seconds and the thermal fuse triggers ...

Example with 2 // capacitor: 25 + 10 = 35 μF

Image

Image

One of the 3 cables to the engine was unsoldered, I sold it back but no change ...

So there is another problem ... I open another subject ...
0 x
Christophe
Moderator
Moderator
posts: 79360
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 11060




by Christophe » 16/07/15, 16:35

0 x

 