Construction of a copper heat exchange coil

Unread Messageby owen » 05/09/08, 13:07

Hello,

I want to build a heat exchanger coil to tigrou sauce (plastic tank rainwater 1000l).

My question concerns the length to provide for the purchase of copper.
How much should be the total length and diameter of the copper?

merci

Edit with moderation: Here 2 simple and fast .xls spreadsheet that will help you:

https://www.econologie.com/calcul-d-un-e ... -3913.html
https://www.econologie.com/calcul-d-un-e ... -3914.html
0 x

User avatar
Christophe
Moderator
Moderator
posts: 46937
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 395
Contact :

Unread Messageby Christophe » 05/09/08, 13:28

Ben impossible to answer without knowing what power you max ...
0 x
Was this forum helpful or advisable? Help him too so he can continue to do it! Articles, analyzes and downloads on the editorial part of the site, publish your own! Get out (part of) your savings from the banking system, buy crypto-currencies!
owen
I understand econologic
I understand econologic
posts: 170
Registration: 03/06/08, 08:16
Location: Belgium

Unread Messageby owen » 05/09/08, 16:08

I plan 10m2 sensors. I am in Belgium.

10kw to 70% will 7kw / h on average
0 x
User avatar
tigrou_838
I posted 500 messages!
I posted 500 messages!
posts: 573
Registration: 20/10/04, 11:25
Location: Lorraine border luxembourg

serpentine

Unread Messageby tigrou_838 » 05/09/08, 16:15

Hello

to give a quick response before disconnecting.

Pipe 25metres in 20 / 22 round. (Small correction)

may be the other person will refine the length or diameter.

tigrou : Mrgreen: actually doing this saucer by rain.
0 x
bobono
Éconologue good!
Éconologue good!
posts: 355
Registration: 08/09/07, 16:58
Location: bretagne
x 1

heat exchanger

Unread Messageby bobono » 05/09/08, 19:47

Image

Image

Here are two heat exchangers a water water and other refrigerant water. iL is deformed by heat.
0 x

User avatar
Christophe
Moderator
Moderator
posts: 46937
Registration: 10/02/03, 14:06
Location: Greenhouse planet
x 395
Contact :

Unread Messageby Christophe » 05/09/08, 19:54

They are given for how kW for which delta T ° and speed?

You sell them ??
0 x
Was this forum helpful or advisable? Help him too so he can continue to do it! Articles, analyzes and downloads on the editorial part of the site, publish your own! Get out (part of) your savings from the banking system, buy crypto-currencies!
owen
I understand econologic
I understand econologic
posts: 170
Registration: 03/06/08, 08:16
Location: Belgium

Unread Messageby owen » 05/09/08, 21:55

25 meters.

No, I do not believe.

I thought 6 meters. 25 20 meters in diameter here costs how much?

they sell to DIY by length of 3 meters Loop is 2m law.

Make welding is dangerous with time his risk of breaking with the heat in time? I am wrong.

And connections seamless I saispas what happens soaked in water at high t °.

here costs a fortune in spare cable length.

The exchanger plate is not it more economical?
0 x
User avatar
elephant
Econologue expert
Econologue expert
posts: 6646
Registration: 28/07/06, 21:25
Location: Charleroi, center of the world ....
x 4
Contact :

Unread Messageby elephant » 06/09/08, 22:39

the plate heat exchanger, that's fine, that's what we used in compressed air dryers, but here do not grow on trees in the market accessible to individuals.
exchangers, I have seen at fairs: 5 or 6 towers 30 cm diameter
welds: tin soda + 5% silver, it's fine, if not, if you can, acetylene oxygen soda, phosphor copper rod: that's what we use for our refrigerating machines: it's more than 10 bars! , sometimes 30. Guys are impressive to see: they heat the red connection, remove the flame, place the rod, all by itself (correction: we inject a mixture of nitrogen with 5% hydrogen under low pressure during the welding: after , the inside of the tubes is nickel!)
0 x
elephant Supreme Honorary éconologue PCQ ..... I'm too cautious, not rich enough and too lazy to really save the CO2! http://www.caroloo.be
User avatar
loop
Grand Econologue
Grand Econologue
posts: 816
Registration: 03/10/07, 06:33
Location: Picardie

Unread Messageby loop » 07/09/08, 07:41

Hello

A small plate exchanger costs about 300 euros
In this case you need a second pump to circulate water from the ball, but it breaks the stratification.
It is rather used for heat exchange with chlorinated pool water which must not circulate in any material

A+
0 x
martien007
I posted 500 messages!
I posted 500 messages!
posts: 565
Registration: 25/03/08, 00:28
Location: planet Mars

Re: coil

Unread Messageby martien007 » 07/09/08, 11:31

tigrou_838 wrote:Hello

to give a quick response before disconnecting.

Pipe 25metres in 20 / 22 round. (Small correction)

may be the other person will refine the length or diameter.

tigrou : Mrgreen: actually doing this saucer by rain.

that's quite a "pipe". You have not deceived you? do 25m this coiled pipe can enter a 1000l tank (dims X = 1m 1m 1m X ???)? It remains the 1000 in the tank may well least once the hose to the intèrieur?